My faucets have been spitting some air for the last few weeks.
Hard to pin down if it is only after sitting not used all night or during frequent use. Seems to do it both times.
It is similar to shutting off the water for a repair and then having it spit when you turn it back on, except not quite as bad.
Pump is 220 V and at least 12 years old. It has a bladder pressure tank
that I put in 8 yrs ago. I am not sure what the air pressure is supposed ot be on the tank, I lost the sheet.
I have checked for leaks at barn and shop and see no moisture near buried lines going to these buildings. I did have the bright idea to bury the line 8-9 feet deep since I had a free backhoe so maybe it will be a while before the ground gets wet at the surface. I also listened to the well control one night and did not hear the pump run when no water was being used.
Any ideas???
 
Your water has lots of air dissolved in it and is releasing some air as the water warms up in your plumbing once inside the house. Particularly in the water heater! Cold water holds more dissolved gas than warm water, just like soda pop.

The excess air either occurs naturally in the aquifer your water is being drawn from or is being absorbed in your pressure tank due to a ruptured bladder. You wouldn't be getting air inside the lines due to a leak, too much water would be squirting out for any air to enter.
 
My family had a well growing up, and the holding tank didn't have a bladder on it like the newer tanks do. Over time, the air level in the tank would increase and when the water level got low before the pump would turn on, air would come out into the lines. Also, they had a pinhole in the incoming line and everytime the pump would turn on, it would pound some more water into the tank. Over a short period of time this lead to air in our waterlines.

One fix would be to turn off the pump and completely drain out the water/air in your tank and repressurize with compressed air.

Just a thought!

Mike in La Crosse, WI
 
Yep I'd go to the bladder tank,drain it and put some air pressure in it.Mine at my old house would need to be drained ever 6 months.Water leaked into the top part of the bladder.Or find some one who can look at the system real quick.Kevin
 
Anyone know what the air pressure is supposed to be?
It is a maroon tank from Menard's don't remember the brand
or required pressure. I'm at work, can get the brand tonite if necessary.
It's the cold water so the heater is not compounding the problem if it's trapped air.
 
You should be able to determine the operating pressure if you have a pressure gauge at the tank. Watching the pressure gauge, run water until the well pump kicks on - that's your low pressure setting. Turn the water off and watch the gauge until the pump stops - that's your high pressure setting.

If your well pump is coming on too often, there is too much water in the pressure tank. You'll need to addair to the tank to displace the extra water.
 
Your initial air pressure should be whatever the lowest setting is on the pressure switch, regardless of the make of the pump. That will assure the most volume per cycle.

It's been over 50 years since I worked on one of the early submersible pumps but some had a unique system to add air to the tank. The line had a check valve and Schrader (snifter) valve near the tank to admit air and the drop line had a drain hole. For every cycle the line would slurp in a gob of air to be shoved into the tank on the next cycle. On the side of the tank was a float valve to let the surplus air out. This was called an Extrol valve. This system was intended to solve the opposite problem, the air in the tank being dissolved by the cold fresh water under pressure. That's the reason for bladder tanks... to keep the air and water separate.

Is your problem a new one? You may need a tank with an extrol valve instead of a bladder.
 
It just started a week ago and is so intermittant that it is hard to
find a pattern, such as only does it after sitting or only does it after washing three loads laundry etc. I do know it is only the cold, I can hear it when the toilet refills, the kids have it happen occassionally when they wash their hands. They use cold only, I use hot only and it doesn't do it for me.
I replaced the old waterlogged galvanized tank about 8 yrs ago with this bladder type and have had no problems til now. No other plumbing changes since Aug when I replaced a bath fixture, no air spits from AUg (and before) to Early Nov.
 
10 to 15 lbs of air pressure in the bladder. You will of course have to drain the tank, pressurize the bladder, then turn on the pump.
 
I have 2 thoughts, one is that the bladder has developed a leak and you are getting air from it. Second one is a pipe from the pump developing a leak along with the check valve in the pump leaking and sucking air back into the pipe.
 
The pressure switches I have worked on and with have been Square D. They recommend 2 psi below the on pressure(low) . So if you have a 40-60 (40 on 60 off)switch your tank should have 38 psi in it . Most of the time it tells what pressure the switch is inside the cover.Unless its fell off. :roll: As did mine in my pump house.
 
Is the water table falling from lack of rain in your area? Is there a nearby new heavy user of water sucking the table down and you are drawing in air from time to time? These are additional thoughts to those already mentioned.
 
Sand on the well point screen ??? Mine spits intermittently, but I'm not sure why. C
 
technova":1iee5bjc said:
Anyone know what the air pressure is supposed to be?
It is a maroon tank from Menard's don't remember the brand
or required pressure. I'm at work, can get the brand tonite if necessary.
It's the cold water so the heater is not compounding the problem if it's trapped air.

About 35 lbs of air in the tank
David
 
Eugene":27qm9xvk said:
Pump in the well sucking air?

My thought too...

I know this post is old but I thought I would add my thoughts....
There has to be air getting in somewhere. Even with the pressure in the bladder at nothing the system should not spit at you. If your air pressure is low in the bladder the pump will kick on seconds after turning on the water in the house.

There are several causes to your system spitting. Intermittent "spitting" rules out several things such as a crack in the poly hose, air leak in your system, etc. The reason I say this is that if you had a small air leak, it would spit regularly (depending on frequent use). If it sat for a long while, and the air leak was past the check valve, you would lose prime.

My best guess without looking at your well and pump would be that there is air at your well point depending on the depth of you well and the age. How old is your well? Water levels change drastically and it sounds as if you are sucking small amount of air from time to time.

Just my 2 cents.
Lyle
 
Do you have a filter system? Filter needs changing or filter that you just replaced is the wrong one and is restricting the flow of water.
 
We lived for a time at a place that had some dissolved methane and sulphur gas in the water. After sitting in the system for some time it would spit gas when the tap was turned on. The water was filtered and tasted and smelled OK. Apparently the gas came out of solution and came to the top of the system.

Don't know if the pressure tank issue took care of your problem. We put a "T" in the line with about a 2 foot vertical pipe and schrader valve to occasionally vent the gas and that took care of it.
 
Sounds like a air intake leak before it reaches the pump. Drain the tank, put 20 lbs of air in the bladder. Go inside and turn on all the highest faucets, like shower, sinks etc.. If you have a pump that needs priming (mine don't, I have a flow well) turn the pump on, prime it until the water squirts everywhere and put the plug back in good and tight. Go inside and wait until all the faucets stop spitting air, turn off the lowest ones first until they are all off. If it still spits air, you have a leak "before" the water reaches the pump, of a busted bladder. As a point of information, I have a 5 gallon tank that takes care of all my water needs. As stated before though, I have a flow well that runs through my pump continuously unless I turn it off to service the pump.
 