Non-cub electrical question

Corky's Cub

501 Club
Good evening guys,

I went to the shop this afternoon to install a new compressor for my sandblasting, and ran into something weird.

It's 240 volts, and the diagrams call for lead 1 and lead 2, plus the common to the mounting switch box.

I had a 240 circuit run to the area for the compressor...one 6ga red, one 6ga black, and one 6ga white.

I double-checked the breakers, and both the red and black are connected to 50-amp breakers, with the white to the buss bar...I know, the wire and breakers are over-kill, but I also plan to run a welder off this circuit.

Here's the weird part: when I checked the voltage of the red and black, each to the white, the red registered 240, but the black only registered 120. What gives?

This is coming out of a 3-phase service panel, and something looks wrong...any ideas?

Thanks,

Corky
 
Is there a junction box between the breaker and the final outlet for the air compressor? If so could be miswired there.

Check the voltages on the circuit at the breaker box, same proceedure you used at the final outlet.
 
Thanks Eugene.

I'll look tomorrow night, but I'm pretty sure it's a continuous cable from the panel to the box. But how could that be? I'm not good with ole Reddy Kilowatt.

Corky
 
I only worked with 3 phase a little, and that has been many years ago, but there were several different wiring configurations that could have been used, so i suggest you contact a qualified electrician. do you have 240 volts between the 2 hot leads? also are you sure the neutral/ground has a good connection at the box. I would also suggest you install a smaller disconnect with breakers close to the compressor to protect the motor in case of overload. The 50 amp breakers will hold till the motor melts down.
 
I think what you have is a Three Phase Delta, 240 volt, 3 wire +ground (three phases and ground)

Red and White legs to the compressor through a disconnect max. of 12 inches away. Black to shop lights and ect through a breaker box.. You would run an isolated ground. The Ground wire from the unit is bonded to the enclosure internally. If the system utilizes an isolated ground, the unit enclosure must be isolated from the panel or load it is being connected to through the use of an insulated conduit fitting. In this installation, a green ground wire from the unit must terminate at the isolated ground bus which is grounded outside the building with a ground spike in the ground.

Please talk to a qualified person before you hook anything up. Make sure you have your equipment grounded properly especially in a shop with moist conditions. You should not run the compressor and the welder on the same circuit. If you use the same circuit, try not to run the compressor and the welder at the same time.

I think there are a couple of electricians on this site or George Willer would know.
 
FWIW, i agree with whats been said so far, get a licensed electrician to wire it up or in the least have the utility co. come out and identify just what you've got. Getting 240 vac single phase from a three phase circuit could be tricky. The three phase utility transformer could either be a
delta or 'Y" configuration with the neutral and safety earth ground affected. This is something that shouldn't be geussed at or fooled around with.

Also 50 Amp breakers for the compressor is not only overkill but potentionally dangerous as already indicated. If you must run both the welder and compressor off the same circuit at least install a second breaker/disconnect box for the compressor with the recommended amperage near the compressor area.
-Ken
 
Thanks for all the input guys.

I was pretty uncomfortable messing with this before posting, and after reading further...now I won't touch it.

I'm gonna have the electrician come in and take a look!

Thanks,

Corky
 