MIG welder question

tractorfan1

Well-known member
Hey guys,

I just bought a Lincoln Electric MIGPAK 140, and was wondering if it would damage my machine if I use an extension cord? Thanks in advance.

Brett
 
Probably not but the size of the extension cord will determine how long it can be. I have an air compressor that will work on a 25 foot cord but will not start on anything longer. I could make it work by increasing the size of the wire in the extension cord. That is what you will have to do. The longer the cord the larger the wire has to be.
 
The magic question is how many amps does it draw! The other magic question is can it be wired for 220. 220 only uses half the amps of 110. These are the determining factors before we get into wire gauge and length.
 
Ok 120 volt 20 amp. How far from the electric service panel, by wire length, not line of sight. That part should be at least 12 gauge. The extension at least 12 gauge wire and preferably 10 gauge, not over 100 feet total if I remember the book correctly. You will need a 20 amp breaker also or a sloblow fuse or fusestat.
 
beaconlight":1951elx1 said:
Ok 120 volt 20 amp. How far from the electric service panel, by wire length, not line of sight. That part should be at least 12 gauge. The extension at least 12 gauge wire and preferably 10 gauge, not over 100 feet total if I remember the book correctly. You will need a 20 amp breaker also or a sloblow fuse or fusestat.

Hi Bill,

I need about a 20' cord. A local auto parts store has a heavy duty 25' 12 gauge 15amp. Is this heavy enough? Thanks.
 
John *.?-!.* cub owner":1c4y1jjz said:
That should do it, another source for cords is camper supply places, they have heavy duty ones

I will try a camper supply store. I read on another forum that running a welder on an extension cord will damage the machine...
 
How far is the Electric panel from the outlet you intend to use? 12 gauge wire is proper for a 20 amp circuit. The question is total wire length and what else is running off of the circuit you put the welder on. Just suppose it is mommas washing machine. No problem except with Murphey's law she will decide it is time for clean clothes while you are welding. Yes washing machines should be on their own circuit. Your welder should be so too. If for some reason the air compressor or garage lights are on the same circuit you have instant overload because the welder uses 20 amps. I hate to be an alarmist but circuit overloads will burn out the equipment or the house.
Use a separate 20 amp fuse 12 gauge wire for the welder. Use another circuit for the lights and a third for the air compressor.
I haven't got to it yet but I will run a #4 wire 120 feet to the garage, with a distribution panel there.
Most extension cords are 18 gauge wire. Air conditiong ones are heavier. The idea of getting one from a camping supply is great. Again it is the total length including cable from the breaker panel.
Inadequate wiring is the same as a brown out by your electric co in the summer. The lower voltage causes higher amperage which causes more heat which burns things out.
 
The panel is about 40' away from the plug in. I would need about 20' of extension cord. The welder is the only thing plugged in. Thanks for the info Bill. :)
 
Brett
I have the same type of welder.I use a seperate plug wired heavy.direct to the panel.I also have a industrial rated extenson cord that i use but only when I have to.I think the extenson was about $30.00 to but.Hope this helps.
:lol: :) Bruce
 