Naw, Eugene - I don't have a neutral. None of the wires are white. I've got two blacks, and an uninsulated copper ground.

Green and bare (no insulation) are the same. White/green/bare wires end up on the neutral buss bar. In this case the uninsulated wire (bare) served the function of neutral/ground. The bare wire should be wired to the center hole/plug on the outlet. If you check the electrical panel, the bare wire should be connected to the buss bar.

At this point. Get a qualified electrician to check the wiring.

Eugene
 
If it were me I would do it my self.
That said from the first question you asked you are not the one to do it. Even if you have to wait get some one to do it for you.
This remeinds me of the boat show story. "How much is the boat?" And the answer is "if you have to ask You can't afford it".
A little knowledge is a formula for disaster.
The 2 blacks and a bare indicate that this was installed as a 220 volt circuit with a safety ground with no neutral. In other words 220 only with no provision for 110 because none was needed.
As far as the coment about Aluminum wire, be advised if so Aluminum is another formula for disaster! The phone Co went through a period especialyl during Korea where we installed Aluminum Buss Bars. Most were eventually replaced. With Aluminum when you get expansion due to heat the wire is slightly compressed. Next time heated you get extra heat because the connection is slightly looser than the last time and eventually leads to enough heat for fire to start.
 
I think I'll certainly leave this one for the electrician. Too many variables seems like.

As to aluminum wiring, I have personally (honest, really, I did it myself!!) replaced a few receptacles, a few light switches, and replaced a few overhead lights with ceiling fans. I've never seen any aluminum, only copper. Guess I have THAT much going for me.

I'm sure, with 36 year old wiring and panel, the whole house probably needs to be upgraded. I think I only have 100amp service. That's based on the 100amp main breaker at the outside panel. I actually have 3 panels - the outside main panel, which appears to control the "heavy stuff" - heat/air, range, stove, etc., etc.. Then there is a smaller panel in the washer/dryer utility room that controls the lights, receptacles, well pump, as well as containing the breakers for all those baseboard heat units that have been disconnected. Yet another panel was added about 15 yrs ago when we added on a room and the garage. That panel controls the lights and receptacles in the new room and garage, as well as the two outside receptacles attached to the exterior garage wall. So it's probably a conglomerate of a mess. But, it has worked for 36 years. If it ain't broke, don't fix it.

OK guys, I really appreciate your advice and assistance. It has not gone unheeded. I'll keep you posted. It will be interesting to me to see what the electrician has to say. It will probably be one of the following 3 things:

1. No problem - 30 minute job at the most. :D

OR

2. The two blacks with no neutral do not meet today's code - I'll have to run a new line instead of converting the 220 to 110 :(

OR

3. Go ahead and call the fire dept. :oops:

WHOA!! Believe it or not, the electrician called as I was typing. Told him what I needed. He said instead of the conversion, he will probably just go under the house, find a 110, and extend it to the new cooktop. He said it should be more than enough to power the gas cooktop ignitor.
Opinions?
 
He said it should be more than enough to power the gas cooktop ignitor.
Opinions?
Duh, That's even a better idea :idea: Never thought to ask about your house structure in regards to a crawl space, or basement below the kitchen.

I'm stuck with have a 2 story house on a slab. To add anything sometimes requires me to take drywall down.

He's probably right that if the new gastop only needs enough power to "light" the burners, it won't require much. And tapping into an existing 110 circuit would suffice, as you won't be using it that often anyway, Right?
 
Yes, thank goodness for the crawl space.....

No, only time that power will be required is when the knobs are turned to "light". I wouldn't think that would take that much juice. Seems similar to my gas grill out on the deck - that ignitor is powered by an AA battery!!
 
beaconlight":k4mkc4yr said:
The 2 blacks and a bare indicate that this was installed as a 220 volt circuit with a safety ground with no neutral. In other words 220 only with no provision for 110 because none was needed.

You currently have two blacks and a bare wire. Ask your electrician if he will tape both ends of one of the black wires with white tape indicating a grounded conductor (neutral). "Should it become necessary to change the actual color of the conductor to meet Code requirements, the electrican may change the colors."

This will provide you with a black (hot conductor), white (grounded conductor) and a bare wire (grounding conductor). You will then need to change the outlet in the kitchen to 110V and remove the 220V breaker and install a 110V breaker.

Cooktop ranges frequently utilize a 110V circuit to control the heating elements. Older style cooktops utilized a combination of 110 and 220 volts in series or parallel to achieve a number of heat setting for the element.

In any event. The existing wiring is not up to current Code. My guess is that it probably wasn't in 1971.

Eugene
 
Well fellas, the job is done. We are cooking with gas, literally.

Gas Co was done in about 2 hours. Waited 2 more hours for the electrician to show up. When he arrived, he didn't mess with the 220 line at all, other than to trim and tape it good, then put the cover plate back over the box. There was an above-countertop 110 receptacle about 5 feet away. He pulled that from the wall, and basically fished line from it to below the countertop. Installed new below countertop receptacle, attached the fished line, and was done. As always, what seems to be a difficult job turns out to be easier than expected.

Again, thanks for all the advice and suggestions. By the way, that 220 line, according to the electrician, WAS 60amp aluminum. He said, more than likely, all my 220s were aluminum, but it appeared all the other lines, from what he could see, are copper. Go figure.
 
Just a dumb electrical question...

What's wrong with aluminum wiring? Did it melt? Was it hard to work with?

Just wondering!

Mike in La Crosse, WI
 
Did it melt
You got it, while aluminum works as a decent electrical conductor, when ever you have current flowing, heat is produced. Aluminum conducts heat/cold differently than copper and other metals. Back in the late 60's & early 70's, someone got the idea to use it instead of copper, as it was probably a cheaper product plus it does weigh less. There's also an interaction with aluminum and other metals too that add to the problem. In order to use aluminum and electrically join it with copper, you need to use a special paste/grease that helps counteract the corrosion that can occur. That corrosion that happens also makes the electrical connection bad, which can cause more heat, thus a fire.

When it was discovered later that fires were being caused due to the wiring, it was banned and copper again became the norm.

One thing that most people don't realize is that the main lines running along the poles, and possible from the pole to your house, are normally aluminum.
 
Mike - aluminum wiring mixed with copper / brass fittings and other wiring causes a reaction that creates corrosion because of the dis-similar metals. This corrosion progresses over time causing poor electrical contact which aggravates the situation. It can eventually progress to a point where it becomes a fire hazard. This problem was not detected until lots of aluminum wire was already in use. In some cases, a paste was applied to the contact surfaces to exclude oxidation but the only real effective correction was to replace the aluminum cable.
 
Hey Mike,

From what I understand, aluminum expands when it gets warm, contracts when it cools off. After going through several of these cycles, the connections have a tendency to loosen, which could result in a short or possibly a fire. Copper, on the other hand, does not seem to have this characteristic. I think the reason aluminum was used is due to its cheaper price.

This thread certainly proves I ain't no electrician, but the above is what I've heard about aluminum. I'm sure someone else more knowledgeable than me will jump in.
 
Bigdog":18ib8tyx said:
Mike - aluminum wiring mixed with copper / brass fittings and other wiring causes a reaction that creates corrosion because of the dis-similar metals. This corrosion progresses over time causing poor electrical contact which aggravates the situation. It can eventually progress to a point where it becomes a fire hazard. This problem was not detected until lots of aluminum wire was already in use. In some cases, a paste was applied to the contact surfaces to exclude oxidation but the only real effective correction was to replace the aluminum cable.

WOW! Did they ever make connectors that were also aluminum to try to correct the problem with the dis-similar metals?

I live in an OLD house (1895) that still has some of its knob-and-tube wire, so thankfully, no aluminum. We are slowly but surely replacing all of the knob and tube in the house with good new 12g copper, though. You should see how they ran the wire and where it went!!! (gotta love old houses and cobbled up systems!)

Mike in La Crosse, WI
 
I wired my own shed with 220 for welding and 110 for lighting and running power equipment. Soon after i built a 48'x24' addition on the house. I went to home depot and got two books a basic plumbing book and a basic electrical book(for doing 3 way switches) I did the whole job myself and it passed inspection. I hired an out of work framer and he and my two sons with me framed the whole thing too.

At the time i was quoted about 28k just for the framing/structure. I did the excavating, foundation, framing, electrical and the plumbing plus paid the asphalt guys for the driveway and it cost me a total of 18K. I insulated the cement floors/walls, added a new bathroom(full bath) plus put R12 9'x9'doors on the 24'x28' garage too. I put 5/8" sheetrock thruout the whole place too. You can learn alot by those books and save many $$ too.

With my new house in the country my boiler was set wrong on the temps and my well pump switch was bad too. The furnance and pump were always running. The plumber i had come to look told me i need a new pump that costs $900. By the time he left the estimate was up to 3k for work that needed to be done.

I readjusted the on /off settings on the boiler for water temp and replaced the pressure switch on my water pump that had a clogged tubing that was connected to it. Now both run very little for a total of $17. I trust no one now I do it myself if i'm not sure i'll buy a book or look on the net and learn how to do it.
 
Aluminum wire came about du-ring the Korean war. Copper was scarce because of military needs and aluminum was available and cheaper. The heat and expandis the crux of the problem because the aluminum is soft and crushes to some extent. The next heat up is hotter because there is a loose connection and it goes down hill from there till the fire department arrives. As far as copper feeds to a house the fact they are areal lets them disapate the heat so no harm happens. The electric code permits smaller gauge wire when it areal.
 