electric problem

john2189

501 Club
I have a problem with the electric in my workshop. Its always been this way, when my air compressor starts, it puts out all the flouresant lights for a few seconds and puts out the outside mercury vapor light. In the day it doesnt mater much, but at night, it gets dark real fast.


The shop is about 100 feet from he house. I have a 30 amp breaker in the house feeding it. I have #12 underground 3 with ground wire goung to the shop. If I change the air compressor to 220 volt, would that help ?

John
 
You have a significant voltage drop/line loss. #12 UF (underground) is rated at 20 amp fuse or breaker.

You need to figure up your total maximum electrical usage for the shop. You can use either watts or amps. Once you have a figure, you can then use a chart titled Maximum distance of circuit as determined by load in amps or watts to figure the line loss and help determine the minimum wire size.

Example from mentioned chart: #12 AWG, (20 amps) will carry 5 amps (575 watts) for 140 feet. 10 amps (1150 watts) for 70 feet. 15 amps (1725 watts) for 45 feet. 20 amps (2300 watts) for 35 feet.
 
You didn't say what the horsepower of your compressor is, but as you can see from the figures Eugene posted, there isn't a lot of available current there. It sounds like your lights & compressor are all operating from the same 120v leg. Changing the compressor to 220v may help with the problem, but the real solution is heavier wiring feeding the shop.
 
I'd have to agree - a #12 wire feed is not nearly heavy enough for what you are doing. It is barely sufficient for lighting and minimum duty outlets. Beef up your feed and install a 50 or 60 amp breaker with sufficiently heavy cable to supply your needs.
 
john2189":2lvaph9b said:
Thanks, looks like ill have to run new wires...
If you want to run anything more than a few lights you definitely need new wires. What size breaker box do you have in the garage now. If none, then you better figure getting a 60 amp panel minimum and run sufficient size wire to feed it. We have a great electrician at our Home Depot who was a great help to me when I wired my barn, not to mention I have two electricians who work for me also who keep me straight..
 
i have the old 60 amp fusebox that came out of my in laws house when they upgraded thier service.

My house service is 125 amps.
 