If the no load is 200 volts, no need to add a load, all you can do is burn the load you just added. The generator is not going to be off that much, load or not unless something else is wrong. I have many 1940's to 1960s generators and most do not have any internal regulation, none would be off that much just from not having a load. This generator is only 4kw because the Kohler is a 3600 rpm engine that has been slowed to 1800 rpm. It is no longer a 12 hp engine. If the engine sounds like it is runing at 3600 rpm then someone fooled with the govenor but I expect it sounds like it is running at 1800 rpms. This generator has a group of resistors and relays that you can check but they do not appear to be the source of your problems. The source likely is the regulator box. I have no idea what is in that box but that is what determines the output. If the engine is running at 3600 rpm then that may be the source of the high voltage but I expect the rpms are correct at 1800 and you need a new regulator. $140 is cheap for that regulator if the price is valid. You can also take apart the regulator box and see what is inside. It may just be a normally closed relay that has stuck.
My non-regulated gen sets may be off by a few volts unloaded, not 80 volts.
Nice gensets, wish I had one, but the electronic regulators can be expensive. If the regulator is potted then you are out of luck, If not then take it apart and try to reverse engineer an fix.
My non-regulated gen sets may be off by a few volts unloaded, not 80 volts.
Nice gensets, wish I had one, but the electronic regulators can be expensive. If the regulator is potted then you are out of luck, If not then take it apart and try to reverse engineer an fix.