big a$$ Kohler genset - questions

midget-farmer

Well-known member
Hey team - I'm normally in the cub forum, but I picked up a great big generator for cheap. Its 12hp so I was told & I got it running today like a top. Electric start only.

Anyway - I had it all warmed up & going & decided to plug in my battery charger & toss it on the battery. After about 3 or 4 minutes the charger started blowing huge clouds of smoke & I had to quick toss it into the snow.

Now - it was a $10 autozone special - but I'm concerned that I may need some sort of voltage regulator or something.

So - how to I tell if I need something there or not? I'm kind of afraid to plug in a freezer as they cost a lot more than the batt. charger.
 
I regulate the voltage on my 3 generator sets with a multimeter.

2 of the gen sets are 120 & 240 volts. I adjust the engine rpms to get 120 volts with the generator loaded. 3rd is strictly 120 volt. Same proceedure - set voltage under load at 120 V.

Guessing - something shorted or wrong with the gen set alternator or the wiring. Might be an easy repair - or not. If you get the set cheap - might be worth repairing.

Also, Harbor Freight has generator heads for sale.
 
Thanks for that - I'll play around with it tomorrow.

I dont know anything about these - but it seems the older they are the less they generate - I'm guessing with a 12hp engine this will produce 3kw - the ID plate is there but its really hard to read.

Plus someone decided to paint it blue - in any case - it fires up & runs great - I must need to figure out this over voltage thing.
 
Were you charging the generator battery while the generator was running? Does it not have it's own charging system for the battery. If so, you were feeding output from the two charging systems into each other. If I have mis-read what you were doing disregard this post.
 
You know Big Dog I was doing exactly that. I just assumed it wouldn't charge its own battery but I guess I need to test that with the multimeter as well.

Dare I hope it isn't messed up?

I need to make a hybrid cub one of these days!
 
Miss read the initial post, thinking the generator head was smoking.

12 hp engine should have an AC output in the 6 to 7 KW range - that is if the gen head is an alternator. If the gen head is the universal motor type, then the output may only be in the 4 KW range.

I would start the gen set up again. Multimeter, check the voltages at each outlet - to see if the voltage produced matches the type of outlet. You can also check the voltage across the battery terminals to see if the gen set's battery charging circuit is still working.
 
My feeling is that the gen set charging system is hardier than the cheapie battery charger. Do as Eugene suggests and check the voltages. Particularly at the battery to see if the gen set is charging it.
 
Tell us more about the generator and check the rating plates, many of that type were old military and were NOT 110/220 volt single phase, though many of them can be rewired to provide that
 
OK - guys here are some details.

Kohler brand
12hp

The plate says the following.

Model = 4CM21
Spec = 10293B
Serial # = 461272
KW = 4
KVA = 4
Hertz = 60
Volts = 120
RPM = 1800
AMP = 33.3
Battery = 12

I'll go out there in about an hour & fire it up & check everything with the multimeter.
 
ok - 13.2 volts at the battery with the machine turned off.
18.0 & 18.1 volts at the battery with it running - with no load.

There is 1 household outlet with 2 plugs.

both ran just under 200 volts with the machine running and no load. 198

I'll load up some pics in a few.
 
midget-farmer":3p5z1vm1 said:
I guess the VR is shot - about $140
May be. Keep in mind that a lot of the older generator sets weren't that good at regulating voltage if they were operating with an open circuit.
 
Put it under a light to medium load and see what the voltage is. I agree with Jim - open voltage on the older gen sets was not regulated very well.
 
I cant decide what to use for a Medium load....

not gonna experiment with my freezer. All my power tools requre me to pull the trigger for them to draw load.

ah... I'll use the big air compressor. It will run for several minutes before it trips off so I will have time to measure the voltage at the plug.

back in a few.

BTW - John - thanks for the manual.
 
midget-farmer":1k70bf2p said:
I cant decide what to use for a Medium load....ah... I'll use the big air compressor. It will run for several minutes before it trips off so I will have time to measure the voltage at the plug.
Hopefully he didn't burn up the air compressor's motor.

I wouldn't suggest using any 120 volt rated appliance on 200 volts. My thought. Purchase 2 plastic fixtures that hold standard light bulbs. 2 each 100 watt filament light bulbs. Wire the 2 plastic fixtures in series. This will divide the generator set's output voltage equally between the 2 light bulbs - 100 volts each.

Before you purchase any parts for this gen set - look over the operator's manual and the service manual. I did a short web search using the model number and receive quite a few hits.

Something else to check. Check the engine rpms - supposed to be 1800 rpm. The Kohler engine will easily operate at 3600 rpms. Check the governor and throttle linkage - looking for binds - faulty settings - etc. See if reducing the engine rpms drops the output voltage.
 
THanks Eugene - I decided to take a nap instead of run the compressor yet.

The govener is right - but I turned up the idle so it is running pretty fast. I dont have a tach I can use to decide what RPM's its running at.

I'll play around with it tomorrow - turn it way down - plug in a couple of shop lights instead of my compressor etc.

I haven't had this much fun in a while!
 
midget-farmer":8q76jtho said:
The govener is right - but I turned up the idle so it is running pretty fast. I dont have a tach I can use to decide what RPM's its running at.
Install a load in one outlet and the multimeter in the 2nd outlet. Turn the idle (and/or throttle or govenor linkage) down while watching the volts on the multimeter.

Hook your shop lights up in series - not parallel. This means you will need to do a bit of electrical wiring.
 
Yea, incandescent lights (regular old style light bulbs) are the easiest to use for load because they are not that critical of how dirty the electricity is, and light bulbs are cheap!

Do NOT use anything electronic or digital (TV, computer, stereo, etc.) on a generator, ever, even a good working one! The electricity from a generator is VERY dirty, fluctuates a lot, and can cause real damage to these types of devices in a hurry.

Also, watch out using microwaves, pumps, compressors, heaters, table saws, etc., which have really heavy startup load. It's easy to place too much demand on a generator and cause damage to these devices because the generator does not have enough power output to get the devices through their heavy startup demand.
 