While working on Earl's car today adding coolant I noticed when the engine was shut off the high and low gauges stayed tight with the operating pressures. My 20+ yrs experience has been that you hear and see the equalization across the orifice for about 30-60 secs. Also that is a way to located the orifice location. I thought he must have a plugged orifice. I have a new Cobalt so I checked it for the heck of it with guages hooked up and got the same results. Nexted I went to my 02 Van and it exibited what I deem normal with a quick equalization after the engine was stopped. I don't know how long it would have taken but after a few minutes very little change occurred in both cars.Is something different about the expansion orifice in lae model cars as opposed to how they used to work. I have changed many tubes in the past so I am familiar with what they look like and how they work but this has me baffled. If I hadn't checked my new car for comparison I would have assumed for sure Earls 96 Skylark was plugged.
 
I got my own answer finally on line. Some models since the mid 90's have TXV's instead of FOT's. That would explain it and why I couldn't find the tube. The TXV is located right on the evaporator under the dash.
 
Are you saying that the newer expansion valves essentially clamp completely shut when power is cut off? Any of the old expansion valve systems I have been around never seemed to work that way. When you shut the thing down, the pressures seem to equalize across both sides of the system.
 
I am not an air conditioner expert, but did work on appliances once upon a time. TXV (thermostatic expansion valves) are an old line technology that had been pretty much abandoned due to higher costs, but have come back into use due to the requests for higher efficiency. They operate depending on bulb pressure, pressure of system, and pressure form an internal spring, and as I understand it, they will shut down once the pressures and temperature lower to a certain point. Running a Google search yielded the following link, as well as numerous others. http://www.hvacmechanic.com/txv.htm .
 
Are you saying that the newer expansion valves essentially clamp completely shut when power is cut off?
Pretty much. I'm sure if I waited long enough I would see some gauge movement but in the short while it was fairly tight. My quess is pump health and OAT and refrig pressure/temp all play a part in how long it would take to equalize.
 
Is it cooling? What is the delta T? Best advice I ever got was NEVER put gauges on an AC system until you can confirm it is actually not cooling. Hoses and gauges plus sealed refrigerant systems equals issues, especially on small systems.
 
A/C systems with thermal expansion valve do equalize in pressure. As you see in the picture, the small red needle is where the pressure was when the A/C system with a thermal expansion valve was when the A/C compressor was turned off. After about ten minutes the pressures equalized.

MVC-013S.jpg


I think the reason why it takes so long for equalization of pressure is because; the thermal expansion valve is the dividing point for the high and the low pressure sides of the A/C system. As the refrigerant passes through the thermal expansion valve, the pressure of the refrigerant is lowered. Due to the pressure differential of the liquid refrigerant, the refrigerant will begin to vaporize at the thermal expansion valve. The thermal expansion valve also meters the amount of liquid refrigerant that can flow into the evaporator. After the A/C compressor is deactivated I have found out it takes 134a refrigerant longer to change “states” to equalize pressure than the older R12 refrigerant. Usually I turn on the HVAC blower motor on to blow warm air through the evaporator to speed the process up.
 