Is anyone fluent with furnace valves. I just installed a new Honeywell gas valve in my furnace but I can't get enough gas flow to the pilot tip to do any good. I checked the pilot pressure and it is maxed out at 4.8 WC
It seems to be a volume problem. And yes, the pilot tip orfice is not obstructed.

Heller1m
10+ Years
10+ Years
Posts: 128
Joined: Thu Jan 03, 2008 11:45 am
Zip Code: 00000
Tractors Owned: 6 Originals, 2 w/sleeve hitches, 2 w/fenders
2-70's, w/fenders, 1 w/sleeve hitch, lights & push blade
100, w/creeper
71, w/fenders
2-122's, 1 w/fel 1 w/creeper & sleeve hitch
2-123's, W/push blades
105,
125,
106, w/sleeve hitch & lights
109

Postby Heller1m » Wed Jan 30, 2008 12:01 am

Just out of curiosity what was the furnace doing that made you want to change the valve?

You have probably already thought of this but, is it possible that you don't have the correct orifice in the valve for the type of gas you are using? Natural gas and propane use different orifices, in my limited experience both come with a new valve, and the correct one must be installed before the furnace will operate properly.

Charles (49) Mo
10+ Years
10+ Years
Posts: 755
Joined: Sun Jan 02, 2005 4:28 pm
Zip Code: 63031
Location: St. Louis Mo.

UPDATE

Postby Charles (49) Mo » Wed Jan 30, 2008 3:06 am

The valve had to be replaced because the coil burned out. I got it working tonight after tweeking and %%(*(()#@ at it for more time than I care. The factory installed orfice said NG, with the LG stuff in a plastic bag.

User avatar
junkman1946
10+ Years
10+ Years
Posts: 761
Joined: Thu Oct 19, 2006 2:31 pm
Location: Cape Cod Ma.

Postby junkman1946 » Thu Jan 31, 2008 5:12 pm

If you have prpane, (bottled gas) you may have the wrong orifice installed NG =natural gas. LG (liquid gas) would be for propane systems. Thats my opinion. Frank
1948 Cub F,1962 Original,1971 C.C.model86, WheelHorse and C.C. mini pulling tractors, C.C. models1450 , 682,106,123, Ariens GT17 with loader,Jacobsen Powermax loader and backhoe 8 more Cub Cadets in the shed waiting to go under the knife and spray gun.

2 Busy
10+ Years
10+ Years
Posts: 227
Joined: Sun Jul 30, 2006 10:55 pm
Location: okla

Postby 2 Busy » Fri Feb 01, 2008 2:55 am

sounds like with the amount of W.C. you have there should not be a volume problem. might be an obstruction in the pilot tube its self.

i assume the pilot worked till the old valve quit. i'd check the tube or the outlet on the valve. seems like they had a wire screen in it that might of cought some trash from the incoming gas line. or too much pipe dope.